Shame its on a D though. Has the client gone for the short run to the board, cos if that is the breaker you need you will be close by on a D32 using 6sqmm
Just done the calcs and its very likely that the existing cct will be outside Earth Loop as the board would need a Zdb of less than 0.05
Just been doing some testing today and spotted a D63, thought oh dear, luckily the machine it fed was next to the DB and it just passed on Earth Loop.
Just done the calcs and its very likely that the existing cct will be outside Earth Loop as the board would need a Zdb of less than 0.05
Just been doing some testing today and spotted a D63, thought oh dear, luckily the machine it fed was next to the DB and it just passed on Earth Loop.