electro

[FONT=Times New Roman, serif]Hi [/FONT]


[FONT=Times New Roman, serif]Can anybody remember the formula for working out ring main cable sizes (Cable Capacities). I know we use 32amp MCB with 2 x 2.5mm² but its been so long I cant remember the formula that proves 2.5mm² is capable of carrying a ring main load.[/FONT]


[FONT=Times New Roman, serif]Thank you in advance[/FONT]


[FONT=Times New Roman, serif]Sorry if this has been discussed before but I have done a search with no results.[/FONT]
 
It >

___20____
Ca Cg Ci Cc


We are allowed to use this formula with the Ib of 20A for ring circuit cables as it is unlikely that the current in any part of the ring circuit will exceed 20A.

Another way is to assume a load of 20A at the furthest point of the ring circuit with an additional 12A evenly distributed so........(32+20)/2 = 26A.


HTH.
 
Last edited by a moderator:
Thanks Lenny

My mind went blank on the matter, I've got the old books out and read the reg 433.1.4 for ring mains, thanks for your answer, with 60 people looking at the post with no answer i dug out the ECA book.

thanks Again Lenny
 
I thought it was always just worked out from table 7.1 of the OSG and the installation method, protective device and max run length (mind i suppose it had to be calculated somehow in the first place :eek:)
 

Reply to formula for working out ring main cable sizes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Thank you for the speedy response! Have seen them on top of plaster in steel conduit before but guess it's not a common desire to have wires...
Replies
2
Views
680
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
999

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top