i have just inspected a couple of buildings & found several problems.

10mm to 2.5mm with no inline fuse/mcb for a lighting cct.

4mm lighting cct protected by 32A Type C leadfing to the Zs falling outside the tabulated values but protected by RCD so gets away with it, not correct i know.

and several other things.

my question is which would be the easiest way for the client to rectify the fist issue, drop in fuse holder/MCB within the JB????

cheers.
 
Last edited by a moderator:
Install any necessary overload protective device where the cable size changes. There will already be a joint of some kind.
 
it goes into a JB then through a connector block.

the two i mentioned are what i would normally use BUT i wondered if there were any other alternatives as we are in the middle of the desert & cannot just pop down to CEF etc.

thanks.
 
The 10mm cable run may be to avoid voltage drop. So long as the circuit ocpd is selected according to the smallest conductor size I don't think this is necessarily a problem.
 
What about 433.3.1 (i) - it's not exactly clear but it could be interpreted to mean that an ocpd for a smaller sized cable could be located on the supply side of the point at which the reduction in size occurs - ie at the CU. Or am I misreading this?
 
It is quite common to run a larger csa cable on large circuits, reducing the csa as the circuit progresses.

As has already been said (post 7), as long as the ocpd is selected with the lowest csa in mind then no further protection will be required
 
433.2 refers to 433.3

You on the right lines, the OP needs to refer to the OPCD and consider it with the smallest conductor size.
Without knowing the current OPCD rating we are all just guessing.
 
it goes into a JB then through a connector block.

the two i mentioned are what i would normally use BUT i wondered if there were any other alternatives as we are in the middle of the desert & cannot just pop down to CEF etc.

thanks.

Screwfix, order before 6pm, its in your hand tomorrow morning:cool::D
 

Reply to Found During I&T in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top