fridge counter in cafe | on ElectriciansForums
Discuss fridge counter in cafe in the Commercial Electrical Advice area at ElectriciansForums.net
i=p/u
Northern Ireland
a guy has rang up this morning and said his fridge counter is blowing the fuse randomly , maybe 20 fuses a week..
i would say there is a motor in this, would you say this is the problem, or what tests could i conduct , as i dont think the megger will show short as only trips randomly..
maybe the stat or something maybe. cheers trev
check trhe rating of the cabinet. it may be that it needs a dedicated 16A circuit..., commando plug/socket.
Turn it up full and clamp it to see what it is pulling. 500v IR it L-E, N-E to check for any obvious leaks. Is it a new bit of kit, or has it been working for years and suddenly started playing up?
Fault-finding is a bit of an artform which comes with time and experience.
Could be anything from defrost heaters, condenser fan motor, evap fan motors, unlikely to be the compressor as they just kick out on the overload klixon, this is a disconnect connected loads one at a time job but my money is on the defrost elements a manky job by the way make sure your tetanus jabs are up to date
,Pict
or just both live conductors to earth....:wink_smile:
Reply to fridge counter in cafe in the Commercial Electrical Advice area at ElectriciansForums.net
If in doubt, hit it with a hammer and see if it gets better. sometimes the simple solutions are the best ones!!
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...