Mates fridge in his shop keeps tripping after varying amounts of time between 10 and 30 minutes he has told me. It is running on a B32 breaker. Should it be a C type? For it to be running for at least 10 minutes before it trips does that mean i can eliminate the problem being high startup current (assumong fridges have one).
 
If the 32 amp mcb is tripping, then either the mcb itself may not be functioning correctly or there is excessive load on that mcb or there is a short later in the function of the fridge

Is the circuit for the fridge shared by other loads ?
If so
How do you know that the fridge is the culprit ?
Could there be an overload of that circuit by the accessories connected

If its on its own circuit,what is the expected load of the fridge ?
Compressor faults simillar to that described ( delayed tripping) are usually neutral to earth faults that trip the Rcd
Has there been any testing carried out ?

Type c would help with start up currents of motors but no doubt it may be the wrong aproach to consider at first
 
Last edited:
If the 32 amp mcb is tripping, then either the mcb itself may not be functioning correctly or there is excessive load on that mcb or there is a short later in the function of the fridge

Is the circuit for the fridge shared by other loads ?
If so
How do you know that the fridge is the culprit ?
Could there be an overload of that circuit by the accessories connected

If its on its own circuit,what is the expected load of the fridge ?
Compressor faults simillar to that described ( delayed tripping) are usually neutral to earth faults that trip the Rcd
Has there been any testing carried out ?

Type c would help with start up currents of motors but no doubt it may be the wrong aproach to consider at first

Can't really add a lot to Des's post only to say that once you upgrade that B to a C your introducing a whole set of problems regarding disconnection times. The Zs for the circuit for a C is nearly half that required for that B, so before you think of changing it you'll have to make sure you can achieve the disconnection.
 
i thought the only difference with b and c type breakers was that b type are more sensitive than c type ie trip quicker wasnt aware of start up currents des please explain cheers des
 
If you have a copy of the OSG then have a look at pg 58 table 7.5 you will see that a B type will trip at 3-5 times it's rated current, so we normally for a modern MCB take the makers recommendation of 5 times so a 6 amp B will trip at 30amps on over current.

A C type as you can see will trip at 5 -10 and again as most makers state 10 we can see that a 6amp will take 60amps to trip.

Most motor, compressors have an inductive load and on start up will have what is termed "in Rush" currents. These can be many amps over the rated size of the MCB and so by utilsing a C type breaker it will avoid tripping.

The different ratings of MCBs were designed to avoid the use of larger than needed MCB's, larger than needed cables ETC for a start up over current that will last less than a second in most cases
 
Mates fridge in his shop keeps tripping after varying amounts of time between 10 and 30 minutes he has told me. It is running on a B32 breaker. Should it be a C type? For it to be running for at least 10 minutes before it trips does that mean i can eliminate the problem being high startup current (assumong fridges have one).

Is there an RCD protecting the circuit?

I would assume a fault on the fridge.

If the hermetics are blocked then this will place the compressor under a heavy load, a breakdown of the winding may be occurring, also check evaporator fan, circulating fan and defrost element, all these may be producing the fault.
 
Haven't been to look at the problem myself yet, just going on his explanation for the moment and trying to get a rough idea of what to look for.
Could the wiring of the circuit be the problem ie loose connections in the plug and socket(s)?
I'll get the make and model of the fridge when I go to have a look and browse the internet to check for the load it pulls.
If there's a compressor fault then that's out of my hands right?
 
UPDATE

Still haven't been to look, but he has just told me that he put the breaker back on today after leaving it off for a while I presume and it has held all day. Dodgy breaker or dodgy fridge it seems?
 
The problem has been the higher temp over the last couple of days. Today is cooler and the fridge works.

I bet the condenser coil is blocked and needs a good clean out. When the coils coils get blocked, the compressor will not work efficiently. The motor run times are too long and the compressor overheats, pulls too much current and...........you guys know the rest.

Tell your mate to ring a fridgeman to give it a good service.

Steve
 

Reply to Fridge tripping. in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
I think over there you would call it a gfci which we call an (RCD) Residual Current Device or RCCB, an RCBO here is an (RCD) Residual Current...
Replies
21
Views
4K
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
Replies
19
Views
3K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K
  • Question
It's ok if you use the correct driver for the application.
Replies
14
Views
2K
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks