M

Malsford

Does the Fronius IG-TL transformer-less inverter have seperated voltage? Im currently fitting one in a garage which has a tin roof, im going to earth the roof to a new spike as the cables pass through it with glands but apparently i need to earth all the frames and rails if the inverter (being transformer-less) doesn't separate the voltage even if the panels are class 2. is this right?
 
According to the dti guide, you should earth your system when one of the following is not met.

-Class II Panels
-Class II cables, junction boxes, connectors
-Transformer-based inverter

The TL inverter does not have galvanic isolation between AC - DC.

On the other hand, inverter's manufacturers say that the TL inverters control any DC injection, or other power quality issues by using DC sensitive RCMUs and surge arrestors. Moreover, TL inverters have passed all the mandatory safety tests defined by VDE 0126, G83.

It's hoped that next updated dti guide will be more detailed in terms of TL inverters.
 
Thats the reason i was confused as i remembered the 3 conditions for earthing but their manual says 'these inverters are designed exclusively for class 2 panels and they should never be earthed'. i phoned a fronius helpline and they told me that it must be earthed (contradicting their manual). Then i spoke to someone for another PV installation company who has just been on the fronius 3 day inverter course and he told me that they said the panels never need to be earthed (contradicting the helpline) Im very confused.
 
Been told its a load of old rubbish by my instructor thats why DTI are altering it, whats happens if the cable breaks away from spike ??? At least on the roof its out of reach
 
there's a difference between earthing the fronius itself and earthing the panel framing itself. Maybe that's why there's a difference in the manual vs helpline. Don't earth the inverter; earth the rails.

I'd agree with the comment that if it's TL and TNCS it's an earth spike, TNS and it's MET. But I'll be looking at the coin----- too now.
 

Reply to Fronius IG-TL in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top