Morning guy's
i am installing a Fronius IG inverter and it states that the max resistance at the ac side from inverter to main service head is max 0.5 ohms, if i have a PME system am i right in assuming the zs at inverter is the zs at board plus max 0.5 ohms for example zs at board 0.35 ohms plus ac cable max 0.5 ohms = max zs at inverter 0.85 ohms
ie max cable cable r1 r1 0.5 ohms
cheers
Presumably this is an IG TL inverter? I don't think it's an issue on standard IG inverters.
Are you getting confused between Zs and Ze? Zs will be the reading at the inverter.
true zs at inverter ze is actually 0.21 and zs at cu is 0.2 zs at inverter is 0.61 so r1r2 is .41 ish
also i have been using fp cable for ac side is this over the top or a requirement, generally clipped direct, if cable clipped dirct i assume no rcd required
thanx for advice
If your doing r1r2 with an isolator at cu end the isolator can give you a high reading, I've found this out a few times.
Agreed, it was, but i sometimes swap "line" onto another pole and it they been alright - all im trying to say, is sometimes high R1+R2 tested through a closed isolater or two can be a reason for high reading.