Just had a Sunday lunchtime call out to a new customer. Bought their property back in May as a holiday home, and have only just switched the heating on. Everything is fine, but come midnight when the economy 7 kicks in, everything goes dead when the RCD trips. I get round and do a quick visual and IR test on the econ 7 board and everything tests as it should. Moving back up-stream I get into the supply cupboard still scratching my head. Tracing the tails, we have L and N entering the meter with L and N departing for the RCD switch. L for the econ 7 leaves the meter via a henly (used as a joint only) off to the CU for the heaters. The supply N however is split at a henly after the RCD switch before going to the main CU and the econ 7 CU. This I explaind is where the inbalance was due to the fact the econ 7 was not being seen by the RCD, however the return N was causing the instintaneous tripping when current flowed.

The DNO have been out and changed the switch telling the customer it was faulty and I have told them to call them back out to sort it.

Im just seeking confirmation I got it right??
 
if the econ7 neutral is taken after the rcd then it will trip, as i think you said. the econ7 is taking live from the supply side of the rcd and neutral from the load side. huge inbalance
 
Last edited:
Just had a Sunday lunchtime call out to a new customer. Bought their property back in May as a holiday home, and have only just switched the heating on. Everything is fine, but come midnight when the economy 7 kicks in, everything goes dead when the RCD trips. I get round and do a quick visual and IR test on the econ 7 board and everything tests as it should. Moving back up-stream I get into the supply cupboard still scratching my head. Tracing the tails, we have L and N entering the meter with L and N departing for the RCD switch. L for the econ 7 leaves the meter via a henly (used as a joint only) off to the CU for the heaters. The supply N however is split at a henly after the RCD switch before going to the main CU and the econ 7 CU. This I explaind is where the inbalance was due to the fact the econ 7 was not being seen by the RCD, however the return N was causing the instintaneous tripping when current flowed.

The DNO have been out and changed the switch telling the customer it was faulty and I have told them to call them back out to sort it.

Im just seeking confirmation I got it right??

Superb peiece of fault finding top notch
 

Reply to Front End RCD Switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
394
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
692
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top