My new house has four floors including a basement and an attic. I have been inspecting the wiring of the sockets circuit. There is a single socket circuit which has a 32amp (6kA type B) MCB. An RCD is installed. There are 26 sockets. I disconnected the live conductor(s) at a socket and then tested each to see which was live before reconnecting them and repeating the process at the next socket with the following results (and inferences):
AA) 1 socket – 3 connected cables, 1 live (radial type connection supplying two radial type connections);
BB) 4 sockets – 3 connected cables, 2 live (ring type connection supplying a radial type connection);
CC) 4 sockets – 2 connected cables, 2 live (ring type connection);
DD) 10 sockets – 2 connected cables, 1 live (radial type connection supplying a radial type connection);
EE) 7 sockets – 1 connected cables, 1 live (radial type connection - end);
FF) 1 fused supply connection to boiler – 1 live connection (radial type connection – end);
GG) 1 fused connection to bathroom fan (not investigated);
HH) 1 fused connection to toilet fan and ceiling light (not investigated).
All the cabling has 2.5mm live (red) and neutral (black) conductors (or thereabouts – based on comparison to known 2.5 sqmm cable). The cables to CC) sockets have insulated earth conductors. The rest are not insulated (except by enclosure in the grey cable sheath and with yellow/green sheathing inside sockets). All the cabling looks to be in good condition and neatly terminated.
I intend to get advice from an electrician. I suspect he will advise a complete rewire and I may well take that advice. However I am wondering if a reasonable course would be to have the 32amp MCB replaced with a 20amp MCB and disconnect the eight kitchen sockets from this circuit and connect as a new ring circuit fed from a new 32 amp MCB. I would ask to have Zs, maximum fault current and continuity of cpc checked. My question is – would this approach be reasonable?
AA) 1 socket – 3 connected cables, 1 live (radial type connection supplying two radial type connections);
BB) 4 sockets – 3 connected cables, 2 live (ring type connection supplying a radial type connection);
CC) 4 sockets – 2 connected cables, 2 live (ring type connection);
DD) 10 sockets – 2 connected cables, 1 live (radial type connection supplying a radial type connection);
EE) 7 sockets – 1 connected cables, 1 live (radial type connection - end);
FF) 1 fused supply connection to boiler – 1 live connection (radial type connection – end);
GG) 1 fused connection to bathroom fan (not investigated);
HH) 1 fused connection to toilet fan and ceiling light (not investigated).
All the cabling has 2.5mm live (red) and neutral (black) conductors (or thereabouts – based on comparison to known 2.5 sqmm cable). The cables to CC) sockets have insulated earth conductors. The rest are not insulated (except by enclosure in the grey cable sheath and with yellow/green sheathing inside sockets). All the cabling looks to be in good condition and neatly terminated.
I intend to get advice from an electrician. I suspect he will advise a complete rewire and I may well take that advice. However I am wondering if a reasonable course would be to have the 32amp MCB replaced with a 20amp MCB and disconnect the eight kitchen sockets from this circuit and connect as a new ring circuit fed from a new 32 amp MCB. I would ask to have Zs, maximum fault current and continuity of cpc checked. My question is – would this approach be reasonable?