I know that many electricians only carry out quick and basic tests after a CU change, but I thought I'd share this with you.
I am a fussy so and so, as many of you already know, so following a CU change I carry out every test imaginable. Having established no shared neutral, good bonding, good IR checks, etc. prior to carrying out said change, I got stuck in to a full spread of testing after installing it....
Was in the process of carrying out an R1+R2 test on every point in the lighting circuit, when I came across an open circuit at a bedroom ceiling rose... Checked switch, connections etc, but no joy. After half an hour in the loft, found the supply to the bedroom lighting joined in a JB but with the cpc ends not connected, just sitting there happily a few inches apart outside the JB, covered in loft insulation.
This is why I would rather be a few quid out of pocket time-wise, than skimp on testing.
 
Its a bit like not bothering to check the ring circuit at every socket - I always do but suspect many don't

Exactly mate. I was only saying to my wife this morning that I'd no doubt spend many boring hours on a hot sunny day, carrying out all these tests just for it all to be perfect, and then this pops up!
Makes it all worth while :)
 
I know that many electricians only carry out quick and basic tests after a CU change, but I thought I'd share this with you.
I am a fussy so and so, as many of you already know, so following a CU change I carry out every test imaginable. Having established no shared neutral, good bonding, good IR checks, etc. prior to carrying out said change, I got stuck in to a full spread of testing after installing it....
Was in the process of carrying out an R1+R2 test on every point in the lighting circuit, when I came across an open circuit at a bedroom ceiling rose... Checked switch, connections etc, but no joy. After half an hour in the loft, found the supply to the bedroom lighting joined in a JB but with the cpc ends not connected, just sitting there happily a few inches apart outside the JB, covered in loft insulation.
This is why I would rather be a few quid out of pocket time-wise, than skimp on testing.


Good for you Guitarist. This is what testing is for. There seems far too many people looking for reasons not to fully test.
 
One lad I worked with refused to do it claiming he wasn't trained to as he didn't have 2391. I always thought a spark should be able to test his own work, some others refused to test a new install because "You know it's going to be ok" disgusting attitude
 
One lad I worked with refused to do it claiming he wasn't trained to as he didn't have 2391. I always thought a spark should be able to test his own work, some others refused to test a new install because "You know it's going to be ok" disgusting attitude


Quite right Trev all electricians should have a good understand of inspection and testing regardless of being 2391 trained.
How can electrician carry out electrical work walk away and let the tester carry the can if he misses a fault.
At least they have to sign the EIC cert for construction.
 
One lad I worked with refused to do it claiming he wasn't trained to as he didn't have 2391. I always thought a spark should be able to test his own work, some others refused to test a new install because "You know it's going to be ok" disgusting attitude

I think its the "I can't be bothered attitude" - no pride in the work they do, god help them if they ever go down the self employed route in he future...
 
One guy sat in his car one day making up test results and then photocopied the sheets and submitted them for every rewire he did on the decent homes programme. The same guy now has AC status with NICEIC and has guys working for him.
 
2 rcds in a CU = 2 rcd tests
preferably at the device itself or from a nearby socket if easier.

exactly. today another spark tried to tell me it had to be done on every circuit! i normally do it on each ring main(providing theres one on each side), at the socket with the highest ZS normally i figure if it works there it'll work eveythere else.
he said it was being thorough, i said it was wasting time! didn't go down well...
 
question, do you do the RCD test on every circuit? or do you just do it on one circuit on each rcd (for a 17th board) and duplicate the results?

As long is nothing is plugged in to a socket then there can be no leakage and the test will be accurate.
The CU I just fitted has 7 RCBO's, so 7 lots of tests at the board. Before I finish a job for good I like to do a ramp test on each RCD somewhere in the circuit, just for that last minute "nice" factor. :)
 

Reply to Full spread of tests after CU change. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
441

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top