Hi

Reference Dead tests in 2392-10.In any of dead tests does functional earth lead on RCD. have to be disconnected as per RCBO,s??


I have surface mounted PVC light switches on upstairs circuit with open ended CPC,.s.Will this affect R1+R2 readings?? As they are a little high


Angus.................Still learning
 
Do RCDs have a functional earth lead? I haven't seen any.

If by open ended CPC you mean that it is not connected to an earth terminal in the light fitting, then this will not affect the R1+R2 readings as you will be testing from the end of that CPC.

High readings can often be caused by loose connections, just make sure the terminals are done up securely for each fitting and switch (and in the CU).
 
thanks for that .Have checked RCD( BS EN 61008).Definitely has white fly lead running to MET.The reason for the Question is that in Insulation Resistance Test they advise disconnection of functional earth on RCBO,s would this be the same for rcd fly lead.? RCD: MEM A100 HE

Angus
 
If there is a fly lead then yes I would disconnect it as it would be irrelevant to the testing of the fixed wiring, could cause a false reading and just in case it would fry the RCD!
Just my opinion not really backed up by proof, just same as you; sounds like a good idea.
 
Do RCDs have a functional earth lead? I haven't seen any.

If by open ended CPC you mean that it is not connected to an earth terminal in the light fitting, then this will not affect the R1+R2 readings as you will be testing from the end of that CPC.

High readings can often be caused by loose connections, just make sure the terminals are done up securely for each fitting and switch (and in the CU).
some of the MEMs had em richard....they use em on the big rig for the 2391 n all.....to see if candidates can recognise the presence of functional earths ......
 

Reply to Functional Earth on RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top