Functional testing of MCB's?? | on ElectriciansForums
Discuss Functional testing of MCB's?? in the Australia area at ElectriciansForums.net
South east
It might sound a bit daft but is there any way of functionally testing MCB's?
It's easy to confirm whether an RCD is functioning correctly but is there any way of testing an MCB?
I've just been reading about counterfeit goods and how some MCB's are manufactured with absolutely no working parts inside them at all and that is what led me to asking this question.
Cheers.
As Widdler said if you have over the years set 1000's of MCB's you know what they should feel like when you set them. There is a slight resistance to the action and a click like sound.
The counterfeit ones feel just like a rocker switch, there is no resistance it just holds in and you know there is something wrong. It's lot like a mechanic, he listens to an engine and says that don't sound right, and you look at him and think how does it not sound right, it's experience.
Previously we had different arrangement which was in-house. But, we now use a Portable Tester & Demonstration Equipment for MCB from SCR ELEKTRONIKS.
We even got a fixture (mechanical jig) to just slide on the circuit breaker and the current connections are done with pneumatic that really saves our time.
But what is the cost of one of these portable MCB test sets?? You have been asked this very same question before, but haven't given any indication as to the cost of these units...
I bet that they cost a lot of money. MCB/protective device testers tend to fall into the remit of primary current and secondary current injection test sets.
Primary current injection test sets tend to be used by manufacturer's of protective devices protecting a supply network (11kV+). They can inject kA's of current into a system and record the time it takes for a protective device to operate.
Secondary current injection test sets can be used to inject a smaller amount of current over a period of time in order to measure the operating time of an MCB or relay, or record the amount of current and time it takes for a device to operate in a staged overload scenario.
Either way I would assume at least ÂŁ5k....That said, the MCB tester that MCB-tester looks cool but I'd be interested in a price, too
Cheers.
Or you could take a wander lead from the load side and touch...........................nahh don't go there lol
I can see the interest in testing MCB's but beyond mechanical test of switch and inspection of type,condition etc,you just have accept the given properties from a reputable manufacturer.Like we do with Airbags and Condoms.
No not really, we will be testing both primary and secondary on both all our MV and LV Switchboards. Generally primary injection will test the main current paths through switchboards and breakers, while the secondary injection proves the CT's and associated meters, relay modules etc... We use the megger PS 3000 for our primary injection needs, Not too sure this time round, on what is going to be used for our secondary injection equipment...
I'm with you on the cost of this portable MCB testers.... Not too much different from a MCCB test kit, in operation, except for the current output, and therefore probably cost!! lol!!
See I got one from my department which we procured for 1500US$, but that was for a particular qty that we purchased for test as well as demo. I don't know the unit price, but why don't u ask the manufacturer?
For MCB's it isn't viable to test their operation unless your setting up to do thousands of them. With regard to counterfeiting most manufacturers have a webpage on how to spot counterfeits of their specific brands based on the actual counterfeit items they've encountered.
Reply to Functional testing of MCB's?? in the Australia area at ElectriciansForums.net
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Ah OK, that makes sense. Thank you Avo.