I have my elecsa assessment tommrrow the job I am showing is a loft extension and shower room.
on the shower circuit I have a Zs reading of 0.52 but the Ze is 0.06 and R1+R2 is 0.13
I though my tester was faulty so I had it calibrated and went back today to get the same readings:confused:

Is something that I could fail on???
 
Its a common question and get alot of new people confused you have parallel paths on your earth so its using more than one earth path in this case the water pipe to your shower is probably the parallel path which is bonded pretty good judging by the results, try withdrawing the shower cable from the terminals to test if you want a realistic result or when showing the elecsa guy simple explain why the result is so low, If he sees your understanding of this it usuallly goes in your favour.
As the earth in your cable is the one your testing its probably best to remove cable for the test then replace do this when the elecsa inspector is there and explain why you did it like this.
 
Last edited by a moderator:
that is what I thought Ze + R1+R2 =Zs so my reading should be 0.19. Not 0.52 but the reading is still ok with the regs, so I am hoping it will be ok.
 
Leekemp. The tables would suggest that if your shower circuit is in 6mm+2.5mm, then its length will be about 12m. If you've used 6mm+4mm then the length should be 16m. If, as is most likely you've used 10mm+4mm cable, then the tables say your circuit should be about 20m long. Does this correspond with what you've got?
 
OK so at least you can rule out the R1R2 as the source of the problem. That's a good thing! The issue is with how you're testing. If you're testing with the shower cable connected to the shower, then you're higher result might be explained by the components of the shower itself becoming included in the test. It could be the same as doing a Zs at a socket with stuff plugged in on the socket circuit. I wouldn't worry about it for your assessment. As Darkwood wisely states, if you show the guy that you know how to test, how to check your results are reasonable, and that you know when there is an problematic reading, then you'll be fine.
 
Wouldn't parallel paths give you alower Zs result?
Yes you would i miss read il stand corrected on this one but if the Zs is higher is likely to be a termination slightly loose although it may not be loose enough to concern also the test probe may be been used on the termination screw and in showers amongst other fixtures the can have an anti-corrosion coating which is slightly resistive.
 
It went very well, passed with an A. but I think I will buy a new tester before the next assessment (the funny readings gave me sleepless night's :) )
 
Well done!! I have mine next week and I'm krapping myself!, what questions did the assessor ask you? What tests did he ask you to perform?
 

Reply to funny reading mtf 1502/2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top