Just popped round to a 1st floor flat that wants their electric shower changed. i was in the bathroom (which as one metre from edge of bath to opposite wall) and aske dto see the fuse board the tennant reached up and opened a cupboard to show the incoming cable (piro) meter and fuse board. Whats the story with a fuse board in the bathroom?. Any ideas guys. many thanks.
 
Personally I am against the idea - BS7671 states ALL electrical circuits in a bathroom should be RCD protected, but everything the suppliers side of the RCD obviously isn't RCD protected. If a circuit tripped and the CU was in a downstairs toilet which someone was using they could quite easily get up and reset it without much problem, but if it's in a shower room you are presented with the risk of someone getting out of the shower to touch the CU.

IMO there is also a risk that the door might fall off or get stuck open, in which case you essentially have a consumer unit where there shouldn't even be a light switch.
 
The Bathroom could not of always been there move the head and CCU or move bathroom to the room it was intended to be in. I saw once service head and fuse boards and not enclosed in a spray shop once the guy asked is that ok there. Now let me think about that!
 
One must assume that it wasn't a bathroom when the supply was installed. Very naughty to turn it into one. That said, if there are no socket outlets then it is technically only switchgear in there, which must be outside zones, ie 600mm away from edge of bath or shower. Additionally, you stated it was inside a cupboard. Interesting one to be sure, but I doubt the owners would want the expense of moving the supply.
 
Hi Guy's just to put the cat amoungst the pigeons, I spoke to EDF today (the supplier) and they said that the property is a purpose built maisonette and the head and meter were put in the bathroom when the property was built (1950's) it does not need to be moved, the fuse board must be moved but not the head. I then phoned National Grid who said the samething. What are your thoughts?
 
Electrical equipment in locations containing a bath or shower should be rcd protected, while the service equipment is probably only protected by the protective device at the transformer.
You could get what they're saying in writing and move the CU, although I don't think a bathroom is the best place for a service head.
 

Reply to Fuse board in bathroom in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
😄 It wasn't the worst I seen over the weekend. Took the kids to Cumbria zoo whilst over there, and the toilets by the giraffes just had twin...
Replies
7
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top