Fuse for surge arrester protection | on ElectriciansForums

Discuss Fuse for surge arrester protection in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 15, 2020
Messages
39
Reaction score
1
Location
Zagreb
Hello everyone,
Is there any rule how to determine the size of fuses which will protect surge arrester. I have 3P+N surge arrester, 20kA, and I need to protect him with fuses. But, how to determine the correct size (amper) of those fuses.
tnx
 
Check with the manufacturer's data.

They all need OCPD protection, but for many SPD that is a fuse in the range of 125A-315A so you don't need anything else with a typical 100A supply as the incoming fuses are enough.

Not sure if it comes off a MCCB though, they might have too high a fault let-through.
 
They all need OCPD pro

Check with the manufacturer's data.

They all need OCPD protection, but for many SPD that is a fuse in the range of 125A-315A so you don't need anything else with a typical 100A supply as the incoming fuses are enough.

Not sure if it comes off a MCCB though, they might have too high a fault let-through.
Tnx,
I have distribution board with 250A incoming circuit breaker NSX from Schneider. So if i took surge arrester 20kA and look at his datasheet, there is note that it should be protectet with 80A gG fuse. So It will be OK?
 
I have distribution board with 250A incoming circuit breaker NSX from Schneider. So if i took surge arrester 20kA and look at his datasheet, there is note that it should be protected with 80A gG fuse. So It will be OK?
You will need to put in a fuse of 80A or less then. Or something like a 32A C/D-curve MCB to feed the SPD.
 
If you can, go for the D-curve as lower inductance (smaller magnetic trip coil for the high instantaneous trip current).

SPD performance depends mostly on inductance, not cable resistance. Hence the guidance in the 18th regs on having the total cable less than 1m, and ideally less than 0.5m, from L--SPD--N/E

It also helps to keep the cables to/from the SPD together so you have a smaller "loop area" in the inductor formed by the cables.
 
If you can, go for the D-curve as lower inductance (smaller magnetic trip coil for the high instantaneous trip current).

SPD performance depends mostly on inductance, not cable resistance. Hence the guidance in the 18th regs on having the total cable less than 1m, and ideally less than 0.5m, from L--SPD--N/E

It also helps to keep the cables to/from the SPD together so you have a smaller "loop area" in the inductor formed by the cables.
Thank you for advices. I will go with fuses, because investor wants it. For him it's easier and cheaper to change fuse inserts than CB (in case of damage).
 

Reply to Fuse for surge arrester protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
849
You can get surge-protected 13A plugs such as this...
Replies
2
Views
269
  • Question
That SPD kit looks like it is intended for use with a standard Acti9 board, it's got the neutral link to go onto the busbar stack etc. You...
Replies
4
Views
1K
davesparks
D
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
Hi Did you find out how many connections you are allowed?
Replies
1
Views
635

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks