Apologies for asking more questions but having trouble finding the answers. On this past test paper one question asks for two reasons why you shouldn't place fuses on neutral conductors only. The only one i can think of is that if the fuse went the whole of the system would still be live, what could the other be?

Thanks in advance.

Ben
 
2nd answer is in the q. fuse in the neutral only. there would therefore be no fuse in the line.

edit. that could give rise to a massive fault current with no protection
 
Last edited:
Depending on the loading, if this neutral is common to two or more phases then the loss of the neutral path for star connected loads can result in them effectivly connected in delta...
 
can you elaborate on that oxo ?

Sorry, I should have said a main neutral an a 3 phase system feeding 1 phase supplies. For example, if it becomes disconnected at the TX star point the disconnected neutral cables then form a link between the phases. If you draw it out you will understand.
 
Found in the packaging of a 300W 118mm linear lamp that was made in China:
USING INSTRUCTION Installing or changing the lamp-stand, please severing the electrical. The temperature of kindling the lamp-stand is rather high, it must be installed on the suitable lamp. Don't close to the combustibles.please notice the good ventilative on and radiation when installing. Don't touch the lampstand or wich when then lampsatand working,so as not to scald. In the return circuit of the working lamp, it must be installed fuse, fuse specification with that of lamp identify power correspondence.
I would hope, despite the appallingly bad translation into English, nobody would be stupid enough to take a pair of wire cutters to the supply cable before changing the lamp! However, the last sentence is a greater cause for concern: one would be forgiven for construing 'return' to mean 'neutral' in this context. I have come across many instances in Chinese consumer equipment of the internal fuse (where fitted) being in series with the neutral connection. It seems this is common practice in China - why?
 
2nd answer is in the q. fuse in the neutral only. there would therefore be no fuse in the line.

edit. that could give rise to a massive fault current with no protection
I missed that Tel, just shows you have to read and re-read the question. Probably why i was no good at exams!
 

Reply to Fuse on neutral? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

thank you so much. that worked out. i ended up shorting the live switch and sparks flew, but i recovered and its all working now. :)
Replies
3
Views
274
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top