I have looked at a new job, House with tncs plus additional earth rod connected into the earth tag on the service fuse. House out in the sticks so I guess the DNO thought 'belt and braces'
They want cable to connect detached garage, will be using swa and separate earth rod for garage (not exporting the the pme) As the swa has mechanical protection, I do not need to protect it with an RCD ?
Would you use a switch fuse to isolate the supply or a two pole MCB. They would be in an external ip rated box close to the meter box behind a large shrub. The rcd can then go into the c/s within the garage.
Or would you fit an rcbo as isolator and not one within the garage.
I just wanted some feedback from others.
Thanks in advance for the usual quality advice