J

Jimmyb

Just wondering after doing a job today, what is samllest fuse size you would use for sockets in a kitchen if there wasnt a washer or dryer in there ?
I put a 32a mcb with 4 double sockets and a single and when all finshed i did think with the loads present surely a 25 or 20 mcb be ok. I always had drilled into me 32 for kitchen no less for years even if there is no big app.
 
I do like 6mm for cookers tho cos i always think someone will install a hob and oven at a later date and say ive put loads of hobs and oven on the cooker circuit and it been fine for years.

I do always run 2.5mm for ovens and 4/6mm for hob on rewires now just because i think it better to have them seperate
 
When will you young electricians get it through your head, MCB's are sized to protect the cable, not the dammed loads!!!

Why would you possibly want to de-rate a perfectly sound FRC, what are you going to hope to achieve, by putting a 20A MCB on a FRC then??
 
When will you young electricians get it through your head, MCB's are sized to protect the cable, not the dammed loads!!!

Why would you possibly want to de-rate a perfectly sound FRC, what are you going to hope to achieve, by putting a 20A MCB on a FRC then??

I know the mcb is to protect the cable but isnt the cable selected based on the load.

I wouldnt derate a (FRC do you mean RFC and besides who mentioned them n e way) i would of maybe used 2.5mm instead of the 4mm
 
I'm with E54!!

The rating of your protective device MUST be more than your Design current (>IB) and at the same time less than your current carrying capacity of your cable taking into account the appropriate reference method.

The only time I derate the protective device for a general power circuit is a) if it's a radial on 2.5 cable
B) if the ring cpc is broken and cannot be repaired ( I have had a couple of occasions where the cpc's have been cut out) so I have left the ring intact and de rated the mcb to allow for the slightly higher Zs value.
 
if cpcs are cut, how does that allow a fault path back if you wouldnt mind explaining , i know i missing something simple..
I'm with E54!!

The rating of your protective device MUST be more than your Design current (>IB) and at the same time less than your current carrying capacity of your cable taking into account the appropriate reference method.

The only time I derate the protective device for a general power circuit is a) if it's a radial on 2.5 cable
B) if the ring cpc is broken and cannot be repaired ( I have had a couple of occasions where the cpc's have been cut out) so I have left the ring intact and de rated the mcb to allow for the slightly higher Zs value.
 
The last time I faced this, some moronic diy'er had cut the cpc's out ( I assume they cut em too short so just chopped em out)

So I had end to end continuity on L-L and N-N and broken on cpc. So removed socket from the point that the cpc's had been chopped, re instated l&n with wagos and fitted a blanking plate.

De rate breaker to 16a so all sockets have a fault path back on either leg al be it with a higher Zs
 

Reply to Fuse size in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top