can you tell me what certificate i need to give to the customer after changing there consumer unit and the extent of the test that i do ??
What if things are wrong with the installation when you doing the test ? Got elecsa 1st inspection tommorrow and had fuse board change but results not the best ??
Any info will really help
Cheers lads
Extent of the tests: You must test every circuit in order to fill out the schedule of test results. ie:
r1, rn, r2 for rings
R1+R2 or R2 for all ccts
IR, Zs and polarity
These should all be done before you start replacing the existing board.
RCD tests once the new board is in.
Reply to fuseboard change in the Australia area at ElectriciansForums.net
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...