I am in the process of a job (first time) to convert from one fuseboard to two fuseboards due to physical constraints. Each fuseboard has its own RCD . Each fuseboard is supplied from same meter tails and linked from one to the other. I am finding that when I test the circuits on one fuseboard, the RCD on the opposite fuseboard is occasionally tripping too??? I understand that the two RCD's are in parallel but not sure how to correct this. PLEASE only reply if you are going to help thanks.
 
What tests are you trying to carry out? what test instrument are you using?
 
try switching one board off while testing the other, and vice versa.
 
You need to post a picture to show the set up as your description isn't totally clear.

What you are correct about is not having 2 RCD's in series.

And why are you doing this?
 
I am in the process of a job (first time) to convert from one fuseboard to two fuseboards due to physical constraints. Each fuseboard has its own RCD .

Each fuseboard is supplied from same meter tails and linked from one to the other
.
Implies the boards are in series.

I am finding that when I test the circuits on one fuseboard, the RCD on the opposite fuseboard is occasionally tripping too???

I understand that the two RCD's are in parallel
Now says they're in parallel.

but not sure how to correct this. PLEASE only reply if you are going to help thanks.

Pointless continuing without further input!!!
 
So in 2009 you set up your domestic business and its now 4 years later....... surely this is a walk in the park
 
So what IR testing did you do before installing these new 'fuseboards' and what testing did you do to ensure that there was no interconnection between the circuits on one board and the circuits on the other?
 
I am in the process of a job (first time) to convert from one fuseboard to two fuseboards due to physical constraints. Each fuseboard has its own RCD . Each fuseboard is supplied from same meter tails and linked from one to the other. I am finding that when I test the circuits on one fuseboard, the RCD on the opposite fuseboard is occasionally tripping too??? I understand that the two RCD's are in parallel but not sure how to correct this. PLEASE only reply if you are going to help thanks.

Can we say we'll only respond IF YOU provide us with a sensible description of what you've done, tested and a photo or 2 - otherwise you will get heaps of flack from all over the place
 
This is a diagram of various possibilities that may help you to identify how you have wired the two CUs.
From what you describe the RCDs are in series so you need to ensure that each RCD is supplied from the main supply and not from after another RCD.
Linked supplies.jpg
 
Sorry all been busy with family stuff.
I have connected them up as per Richard Burns right hand diagram.
Also, the series / parallel issue is confusing as the RCD's are across R1 and RN although but in series in one of the diagrams above.
So, looking at that diagram (and following the circuit with both RCD's and main switches on)both RCD's are across R1 and RN so either could trip during testing as one could be more sensitive than the other???
Does anybody else see that??
 
SORRY, should of read......
So, looking at that diagram on the right (and following the circuit with both RCD's and main switches on)both RCD's are across R1 and RN so either could trip during testing as one could be more sensitive than the other???
Does anybody else see that??
 
SORRY, should of read......
So, looking at that diagram on the right (and following the circuit with both RCD's and main switches on)both RCD's are across R1 and RN so either could trip during testing as one could be more sensitive than the other???
Does anybody else see that??

Not at all - if you follow the right hand drawing the RCD's WON'T affect each other.

So what tests have you done and why are you doing this work?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fuseboards
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
19

Thread Tags

Tags Tags
fuse

Advert

Thread statistics

Created
rob69,
Last reply from
Chrisuk,
Replies
19
Views
3,277

Advert

Back
Top