Fitting a new CU today (domestic TT) and using "Fusebox" for the first time - 14 way Type A RCBO board, 9 ways used 5 spare.

All good until testing RCBO trip times - 7 test perfect, but 2 (both 6A) tripping during half test, 1 @ 0 the other @ 180. All loads disconnected, tested again, same results. I'm assuming these 2 are faulty or have I missed something at the end of a long day?

Ramp test for all 9 RCBOs trips @ 18mA. To my mind this is much too low, but I assume this is the design as they are all the same. (MFT recently calibrated and working fine as far as I'm aware from other tests and recent use.)

Anyone else had any issues with these RCBOs / the brand?

I have another 6 way RCBO board to fit this weekend so a little anxious...

Timotei
 
I have tried a few of the fusebox cu, and rcbo and found them to be really good, and have no problem with contractors using them on any sites I have been involved with, normally given a choice I specify hager if the client wants me to choose/specify otherwise it's fair game, but really don't like bg.

Not sure if they are not available, or just difficult to get, but bg appears to be type ac rcd/rcbo only, which could be an issue.

These would be the first failures I have been aware of with the fusebox kit.
 
Fitting a new CU today (domestic TT) and using "Fusebox" for the first time - 14 way Type A RCBO board, 9 ways used 5 spare.

All good until testing RCBO trip times - 7 test perfect, but 2 (both 6A) tripping during half test, 1 @ 0 the other @ 180. All loads disconnected, tested again, same results. I'm assuming these 2 are faulty or have I missed something at the end of a long day?

Ramp test for all 9 RCBOs trips @ 18mA. To my mind this is much too low, but I assume this is the design as they are all the same. (MFT recently calibrated and working fine as far as I'm aware from other tests and recent use.)

Anyone else had any issues with these RCBOs / the brand?

I have another 6 way RCBO board to fit this weekend so a little anxious...

Timotei
Hi matey


I've fitted a few of the Fusebox boards with no issues at all find the quality as good as all the other leading brands, I fitted a board the other week and another board yesterday all the RCBO's tested at 21mA very consistent I too always ramp test after I've done the Auto RCD test on my MFT just for peace of mind, also found that all my 1x and 5x were very consistent test results
 

Reply to Fusebox RCBO trip / ramp in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
693
davesparks
D
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top