Hi
Just trying find reason for not allowing fused neutrals in a fuseboard if there is one
I know why its dangerous to have fused neutral in service head

A single-pole, fuse, switch or circuit breaker shall be inserted in the LINE conductor only.

OR

Automatic disconnection in the event of a fault will disconnect the supply to the LINE conductor.
 
Years ago both live and neutral were fused,however if a fault causes the neutral fuse to blow then the live stays live leaving a dangerous situation.
 
not just that, phil. if a N fuse blows, then all the neutral conductors on that circuit will be at 240V, as there's no VD due to 0A flowing.
 
Surely it would be because they have no path back to the sub station where neutral is bonded to earth?

only an apprentice so please correct me if my thinking is incorrect.

james :)
 
OK, Dean. think of a circuit. for simplicity, L ( 230V) feeds 1 light, then from the light goes via the N back to the supply N (0V). switch the light on and the supply goes through the load in at 230V and out at 0V. there is a current flowing in accordance with ohms law.

this means that there is a volt drop across the load V=IR.

now, imagine that the N is disconnected from the supply by a blown fuse. the current flow is the zero as it's open circuit.

the VD across the load is now zero so ye have 230V all through the circuit to where the open circuit is, draw it out, it becomes obviuos.

this situation only arises when the load is connected. if it's isolated or switched off , then there's no voltage after the switch.
 

Reply to Fused neutrals in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
896
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
348
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top