T

terryp

I'm connecting a heated towel rail via a fused RCD spur and have now been asked to add a shaver socket. Both are only 3A load so under 13A. The shaver socket is permanently connected but the towel rail is on a timer. Can both of these be connected to the spur via their own 3A fuses. Cearly the load is ok but they would count as fixed appliances. The alternative would be to do the shaving socket off the lighting circuit but then its not on the RCD!
 
Aint the shaver socket selv so doesnt need rcd ?? im prob wrong tho

You still have to protect the cable supplying it if it is less than 50mm from surf...... (blah blah blah) so unfortunatley it will have to go on an RCD, plus all circuits in a bathroom have to be on an RCD regardless of cable depths.
 
The trouble you will have by doubling up on the spur is you will need to rate the fuse for the total load demanded. You say 6A. Therefore it will need to be a 10A fuse, the cables must be rated for 10A. If the towel rail recommends fusing to 3A the chances are the cable connected by the manufacturer will not be rated at 10A.
I'm not a fan of RCD spurs, I always prefer to try and encourage customers to update their consumer units rather than have spurs all over the place. Bit more expense, but much safer.

Sorry, just read again, you did say through 2x 3A spurs.
 
Last edited by a moderator:
Yep: my thinking was I can fuse each appliance with a 3amp fuse thus protecting them. The fused spur wiring would be rated up to 13A so could fuse this at the RCD at 10 or 13A. Thus all is good - only concern is that I thought you were only supposed to have one fixed appliance on a spur - but I cant see whats wrong with having another as long as the total load is lower than 13A.
 

Reply to Fused RCD spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
440
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top