scott.rick

i recently had to add a spur from a ring to supply a item of fixed equipment. I took the supply from a socket into to a switched fused spur and placed the necessary fuse for the equipment directly after the socket then a 10 meter cable run to a flex outlet connection unit then a 0.5m flex cord on the item of equipment.

My QS now tells me that the run is only allowed to be a maximum of 2 meters or else the spur must be changed to a ring and the socket i took the feed from must be re-configured to allow this. He claims this is stated in the regs but i have never heard of this?? i have always thought that provided the voltage drop is not too much and the resistance is within the max zs for the protective device etc then this is acceptable.

has anyone else come across this or if its in the regs can you tell me where it is please??
 
this is where he got the conclusion

BS7671 page 74

433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor in the part of the run between the point where a change occurs ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfills at least one of the following conditions:

(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )

im still unsure if my installation is wrong and i have to rewire it or not????
 
Last edited by a moderator:
this is where he got the conclusion

BS7671 page 74

433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor in the part of the run between the point where a change occurs ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfills at least one of the following conditions:

(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )

im still unsure if my installation is wrong and i have to rewire it or not????

Ok, I'm going out on a limb here but.....

The above quoted part of the regs seems to pertain to installing a protective device after a point where a change ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) has been made, as opposed to the standard requirement of 433.2.1 that states the protective device must be installed at the point of the change.

With that in mind, if no changes ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) have been made before the spur cable reaches the existing FCU, is this particular reg even applicable?

If you replaced the switched flex unit with a combined SFU/FCU as long as the cable connecting that back to the ring, was not subject to any of the changes already mentioned, then surely this would resolve the issue?

I'm probably wrong though :eek: and no doubt someone will tell me why.
 
Maybe it's to do with spuring off a spur. If the guy wants the means of isolation within 2m, the current spur would count as the single spur off the ring the new position would be the second, probably wrong. Think the QS just wants the means of isolation closer.

Having looked again think he does want you to make the first fused spur you put in part of the ring and the second closer flex outlet the spur from the ring and replace the plate with a switched fuse spur.


please can you post any regs regarding spur from spur. would be much appreciated.

Can you spur off the ring for sockets on radial via a FCU then supply some down lights off the same radial if the total does not exceed 13A.
 
please can you post any regs regarding spur from spur. would be much appreciated.

Can you spur off the ring for sockets on radial via a FCU then supply some down lights off the same radial if the total does not exceed 13A.

Have a look in appendix 15 might be something in there haven't got the BRB to hand, don't take it to bed with me;).

You can spur from the ring, then spur from the load side of the 13amp fused spur or one of the additional sockets feed from the first fuse spur, then spur to another switched fuse spur for a lighting circuit fused to 5 amps. christ thats a lot of fused bits getting myself confused :D
 
its not an unfused spur tho its a switched fused spur off a ring and that is different plus the regs only say max number of outlets spured off a ring unfused, isnt it that if its fused you cant put as many as you like as long as it doesnt exceed total fo that cable and protection???

Also OSG p54


The number of socket outlets on a fused spur is unlimited. 13A max.

assumed 20A load with 32A MCB 26A at furthest point.

Q. can you place 2 FCU's on a spur if the total does not exceed 13A

I have asked this on another thread and had no answer really.

Whats your take. would be appreciated.
 
Last edited by a moderator:
Thanks, just wanted some confirmation as I did just that the other day. But started thinking to much and was concerned a DIYer might change the FCU's to sockets etc and increase load on the cable from ring.

lol abt BRB

regards
 
Don't see why not as essentially they could both combined only draw the same amount as a spured double socket outlet.

Opps you changed your previous post sorry :D
 
Last edited by a moderator:
True enough and if a DIYer did make a change it wouldn't be my doing either.

whoops getting late... I meant to put that elsewhere but just put it back. so as was..
 
Last edited by a moderator:
Have a look in appendix 15 might be something in there haven't got the BRB to hand, don't take it to bed with me;).

You can spur from the ring, then spur from the load side of the 13amp fused spur or one of the additional sockets feed from the first fuse spur, then spur to another switched fuse spur for a lighting circuit fused to 5 amps. christ thats a lot of fused bits getting myself confused :D


Like this
spurspur.jpgapp15.jpg
 
Last edited by a moderator:

Reply to fused spur cable length??? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
123
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

no problem then, as mentioned by handysparks the fuse should be changed to a 3 amp, the cable to the fan from the spur need not be too big either...
Replies
4
Views
1K
  • Solved
Please use the like button to thank, like or whatever. As the forum treats that as a positive message then and uses it to score members.
    • Optimistic
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top