I have a Cooker circuit on 4mm T&E using a 32A MCB. I have established that my dining room 3 double socket outlets is wired as a radial spur directly off the cooker circuit using 2.5mm T&E (I didn't do it). I assume this is not acceptable but I was wondering; if I add a 13A fused spur for the spur from the cooker circuit to the dining room will that be acceptable. The sockets in the dining room are rarely used at all let alone used for anything demanding. I know this is far from ideal but any solution that requires additional wiring would be very intrusive.
 
as spin says. also, if the cooker circuit is not RCD protected, i would go for a RCD/FCU. or change the MCB for a RCBO
 
Reg 433.2.2 and 434.2.1, AKA forward fusing :wink_smile:

This set of regs are especially handy for kitchen circuits, where say you need to power a cooker hood, or say an igniter circuit for a gas hob from the electric oven/cooker point.
 
I suppose as long as the circuit can support the loads it is alright.
No one has asked the rating of the cooker.

I don't think anyone would say it was acceptable to connect a cooker to a socket radial.

If there is an integral socket at the cooker switch and a cooker over 5366W the circuit will be overloaded even with a 13A FCU limiting the current to the three sockets.


Edit - Without the integral socket at the cooker switch a cooker of 9200W would be acceptable so this would probably be ok.
 
Last edited by a moderator:

Reply to Fused Spur off Cooker Circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
823
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
906

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
432
I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top