Builder installed 175w / sq metre in an area 6.7 x 3.5. What should the fused spur be rated at and should it have a contractor as well?

Am I correct in thinking it is drawing just over 17A therefore 13A fused spur is insufficient?

Thanks
 
Is the spur (aka FCU) getting warm? I would probably switch it off until you have got to the bottom of things.
 
Its 175W per sqm therefore you have to multiply the mat area by 175W thats why I asked it the area he quoted was the mat size or the size of the room.
 
6.7 x 3.5 = 23.45
23.45 x 175 = 4.1kW
4.1kW / 240 = approx 17A

Depending, as Mike said, whether this is mat size or room area.

OP, is the FCU ('spur') warm?
 
OP, is the FCU ('spur') warm?

ask when he's taken the washing off of it.
 
2 cats shat on 2 mats.

stapled their tails together. Siamese cats. ?
 
We have not heard back from the OP on the size of the mat or room, everything else is guess work, including how many cats are sat on the mat.
 
and a roll of A4 paper to print off the lecy
6.7 x 3.5 = 23.45
23.45 x 175 = 4.1kW
4.1kW / 240 = approx 17A

Depending, as Mike said, whether this is mat size or room area.

OP, is the FCU ('spur') warm?
Thanks everyone, that was the room size....the problem was the fuse was blown and casing burnt...checked with the builder who installed it and the fused spur should have been 20A, but the matting is slightly under the size I quoted making it just under 16A which works for the Stat (but not clearly for the switch).
 
Thanks everyone, that was the room size....the problem was the fuse was blown and casing burnt...checked with the builder who installed it and the fused spur should have been 20A, but the meeting is slightly under the size I quoted making it just under 16A which works for the Stat (but not clearly for the switch).

I think you need to get your builder to pay for an electrician to put this right. And point out to him what he has done wrong - I bet he's done this in other properties as well.
 
Is there any fixed furniture in the room now, if this furniture is on top of the mat this would cause localised heating and lead to a short circuit and blowing of the FCU, lots of variables that can not be ascertained from your posts.

What is the room used for?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Buckinghamshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Fused spur rating for electric underfloor heating
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
HenryCooper,
Last reply from
Timbo,
Replies
24
Views
9,229

Advert

Back
Top