maybe he is flying around on a magic carpet.lol ?We have not heard back from the OP on the size of the mat or room, everything else is guess work, including how many cats are sat on the mat
maybe he is flying around on a magic carpet.lol ?We have not heard back from the OP on the size of the mat or room, everything else is guess work, including how many cats are sat on the mat
and a roll of A4 paper to print off the lecy
Thanks everyone, that was the room size....the problem was the fuse was blown and casing burnt...checked with the builder who installed it and the fused spur should have been 20A, but the matting is slightly under the size I quoted making it just under 16A which works for the Stat (but not clearly for the switch).6.7 x 3.5 = 23.45
23.45 x 175 = 4.1kW
4.1kW / 240 = approx 17A
Depending, as Mike said, whether this is mat size or room area.
OP, is the FCU ('spur') warm?
Thanks everyone, that was the room size....the problem was the fuse was blown and casing burnt...checked with the builder who installed it and the fused spur should have been 20A, but the meeting is slightly under the size I quoted making it just under 16A which works for the Stat (but not clearly for the switch).
Thanks...that is what is now happening.....I think you need to get your builder to pay for an electrician to put this right. And point out to him what he has done wrong - I bet he's done this in other properties as well.
Thanks...that is what is now happening.....
There’s no such thing. 13A is the max fuse as protection from a spur. As above, needs a dedicated circuit. 20A MCB. And a 20A switch.checked with the builder who installed it and the fused spur should have been 20A,
Yeah, but this was installed by a builder.?A room this size would usually be 2 mats split across 2 Spurs / time clicks in my experience