P

Piratepete

Hi
Am reviewing a small Control Panel from China.
The Panel operates a hydraulic scissor lift. One contactor DOL 1ph 230V motor. Limit switches, Up and Down buttons.
On the previous model the 230v/24v 50VA control transformer had fuse protection on both sides, 0.3A for the primary and 2 amp on the secondary.

The new panel has cbs, but only one, 1 amp on the primary side. What requirements are there for protecting control transformers? What is good practice these days? Fuses or cbs? It's a long while since I looked at panel design!

Any help please - much appreciated.

Thanks
Pete
 
either or i think, as long as the protective device is suitable for the task. so a CB would have to be a D type IMO. I would also fuse the secondary, but if the cables are rated to takethe max current from that tx then it doesnt need fusing, but i prefer to. It will protect the tx from a short on the secondary side.
 
Protect both sides. Your control wiring is protected then.

To protect the transformer you need to protect the secondary side. The main double pole cb is 32 Amps feeding the motor contactor. So if the primary is connected by suitably rated wiring to this CB is that permitted without any sub fusing.? I suppose that the risk is of a fault in the primary that doesn't trip the breaker but could cause a fire. How likely is that scenario?

Cheers

Pete
 
The above fuse carriers can be obtained as a direct replacement for MCB's and as such can be used to supply DB's from DBs to afford full discrimination, that can't be achieved by using MCB'S in series.
 

Reply to Fusing for the Control transformer. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top