Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
 
Hi - sorry to be a party pooper, but a BS1363 3A fuse is more sensitive to overload than a BS60898 6A mcb. For example, the 3A fuse will always melt at 6A but the mcb will never trip.

[ElectriciansForums.net] Fusing of fans to comply with manufacturers recommended instructions
 
Manufacturers instructions are usually nonsensical, inappropriate and unattainable; a bit like the serving suggestions on food packaging



Might be nonsensical but as per The Wiring Regulations which in the UK we have to follow the manufacturers instructions supersede the Regulations and the greatest knowledge of all the electrician
 
Might be nonsensical but as per The Wiring Regulations which in the UK we have to follow the manufacturers instructions supersede the Regulations and the greatest knowledge of all the electrician

This is not the case. The regulations ask us to "take account of" manufacturer's instructions. This has recently been changed from the previous wording of "must be followed"

The reason for this is the proliferation of less than useful or appropriate info that is included in some products. Some would ask us to install to lesser standards than BS7671 asks.
 
Might be nonsensical but as per The Wiring Regulations which in the UK we have to follow the manufacturers instructions supersede the Regulations and the greatest knowledge of all the electrician

Rubbish. Manufacturers instructions are for guidance only and yes we have to take account of them. But we do not have to follow them, especially when they are wrong.

In this case,
1. FCUs are not needed or used on lighting circuits which are already adequately protected.
2. A 3a FCU offers no discrimination against a 6a MCB in spite of 'Contacts' post above.
3. The fuse is to protect the cable, not the device on the end of it. It would be non compliant for a manufacturer to fit a cable so small it required 3a protection.
4. How would the manufacturers instructions be complied with in all the other countries where FCUs are neither available nor compliant?
 

Reply to Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
722
Yes, it would give some measure of user protection but probably not in the case of a fire.
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top