G59/3

Morning Guys

I have had a look around on here but can't seem to find what I am looking for.

I need to know what the latest is regarding G59/3 inverters and whether we still need to use a g59 relay!

I have read that 5 or more inverters still require an additional g59 relay, but 4 or less don't.

Please could some kind soul point me in the right direction.

Many Thanks
Mark
 
G59/3 only applies to systems 50kW or below so if your total system size is above this you will still need the relay

Matt
 