what are the new guidelines and where can info be found?i have it up to 4 inverters can be fitted type tested without a g59 being required.5 or more inverters req a g59 relay .is this now in force?
2.3. Connection and Commissioning Procedure for Power Stations above EREC G83/2 limits but less than 50kW or 17kW per phase using Type Tested Generating Units only
In order to simplify the connection and commissioning procedure for Power Stations in this range which fall in general under the same envelope as EREC G83/2 Power Stations in terms of the Micro-generation Certification Scheme (MCS) requirements a simplified application form has been produced which allows the Installer to make the application for connection and to complete the commissioning. This means that the process can be carried out without the active engagement of the Customer who will become a Generator at the end of the process. This is in line with the procedure under EREC G83/2 and is the primary change which helps to meet parts 1 to 7 of the terms of reference.
2.4. Connection and Commissioning Procedure for Power Stations above 50kW which use Type Tested Generating Units only
The connection procedure for power stations of this size has not changed. However a simplified Commissioning procedure has been identified which reduces the need for on-site testing but which ensures that the other commissioning requirements are carried out correctly. This is the primary means to meet part 8 of the terms of reference.