We recently installed a couple of tripower inverters that need to be set to G59 protection settings. Unfortunately they got set to G83 using the dials (5-8-2), which I didn't think would be too much of a problem as I'd picked up on it within a few hours of it being set.
However, I couldn't find any G59 setting for the dials in the manual, and it doesn't seem to give a G59 setting using the grid guard code either.
I'm going to do a firmware upgrade anyway to install optitrac, so I'm hoping the new firmware will have G59 settings on it, but I'm a bit baffled by this as SMA list a G59 type tested approval, and have the test certs etc for it.
I'm thinking of manually setting it to G59 settings, but presume this won't then be type tested.
anyone else had this before / know how to sort it out?
However, I couldn't find any G59 setting for the dials in the manual, and it doesn't seem to give a G59 setting using the grid guard code either.
I'm going to do a firmware upgrade anyway to install optitrac, so I'm hoping the new firmware will have G59 settings on it, but I'm a bit baffled by this as SMA list a G59 type tested approval, and have the test certs etc for it.
I'm thinking of manually setting it to G59 settings, but presume this won't then be type tested.
anyone else had this before / know how to sort it out?