Small update - ENA have published Guidance Note 2/4 which covers details of the transition period from G83/1 to G83/2:
GUIDANCE NOTE 2/4
First issued 03 March 2011 – updated 06 October 2011
Second Issue 29 March 2012
Third Issue December 2012.
ENGINEERING RECOMMENDATIONS G83 AND G59
This guidance note was originally issued on 03 March 2011 and its main provision was to allow the use small scale generation of capacity greater than 16A per phase, provided it had been type tested to the requirements of G83/1-1 but with a modified over frequency protection setting.
It was updated on 06 October 2011 and again in March 2012 to allow the use of suitably sized inverters rated at 16A or less to be used with either G83/1-1 or G59/2-1 protection settings.
Now that G83/2 has been published the Distribution Code Review Panel wishes to see the following continuing interpretation:
• For all small scale embedded generation sets of up to 16A per phase, until 1 March 2014 it is permissible to connect to the general requirements of previous versions of G83 provided this is through an inverter or controller with a protection/control system that has either been fully type tested in accordance with G83/1-1, G83/2 or in accordance with G59/2. After 1 March 2014 it will only be allowable to connect small scale embedded generation of up to 16A per phase that complies with G83/2.
• Any application for connection above 16A per phase made on or after the 03 March 2012 must comply with the requirements of G59/2-1 in full.
The full updated Distribution Code v19 (of which this is a part) is available here: