I'm currently doing some galv lighting trunking all wired in low smoke singles with metal fire clips installed in the trunking over the escape route. I have been supplied plastic lid by the main contractor is there any thing in regs about not being able to use this. Sorry would look in my byb but as working away and traveled with someone else it's a bit hard when it's at home I really appreciate your help stu


Sent from my iPhone using Tapatalk
 
Don't know any reason why you cant use plastic lid as long has you have the metal retaining clips so the cables dont full out if the lid was to melt , afterall you can still use yt2 amd yt 4 plastic mini trunking as long as you use the retainging clips, unles metal lid has been specified by the designer.
 
Last edited:
Galv trunking should have a galv lid?. Think I have seen it many years ago.Nothing wrong with using plastic and singles either, the only concern I would have, no mechanical protection with plastic maybe not even with a lid?, what is the environment and situation of use.
 
Just didn't know if there was anything to say about the plastic lid on it falling and causing a hazard but I guess I'm just over thinking this as the light fittings are plastic back all though held on by clips I'm sure a plastic light melting and hanging is more of a hazard then a 1,5 m bit of plastic lid


Sent from my iPhone using Tapatalk
 
Galv trunking should have a galv lid?. Think I have seen it many years ago.Nothing wrong with using plastic and singles either, the only concern I would have, no mechanical protection with plastic maybe not even with a lid?, what is the environment and situation of use.
All lighting trunking i have installed has had plastic lid , athough i have seen metal lid in the past
 
You should also consider whether the PVC lid is flame propagating and whether it would release toxic fumes.

I would far prefer to see galvanised lid to be honest.
 
You should also consider whether the PVC lid is flame propagating and whether it would release toxic fumes.

I would far prefer to see galvanised lid to be honest.

I don't see the relevance unless the designer has spec'd metal.

It's going to be full of PVC singles isn't it?
 

Reply to Galv lighting trunking in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
675
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top