Hi, just quickly im a new, young but enthusiastic spark : D so some of my questions might sound obvious but bare with me : )
Im looking to install a small DB in a garage which is 4 way, a DP 40A incomer with a 16A radial mcb and a 6A lighting mcb (you know the type) anyway.....
The incomer is 40A therefore im lead to believe due to discrimination the mcb at the main Db should be 40A or bigger. My problem is this, without any correction factors, to carry atleast the 40As my breaker will be rated at I need to use 6mm cable.
However the load of my small DB is only 16A plus (using diversity) 66% of 6A being roughly, only 20A. Now if my breaker at the main board were a 20A or 32A I would beable to use a 4mm or even 2.5mm cable and it would still be protected.
As I say to most experienced sparks the answer is probably straight forward but any help is appreciated.
Thanks
r10ley
Im looking to install a small DB in a garage which is 4 way, a DP 40A incomer with a 16A radial mcb and a 6A lighting mcb (you know the type) anyway.....
The incomer is 40A therefore im lead to believe due to discrimination the mcb at the main Db should be 40A or bigger. My problem is this, without any correction factors, to carry atleast the 40As my breaker will be rated at I need to use 6mm cable.
However the load of my small DB is only 16A plus (using diversity) 66% of 6A being roughly, only 20A. Now if my breaker at the main board were a 20A or 32A I would beable to use a 4mm or even 2.5mm cable and it would still be protected.
As I say to most experienced sparks the answer is probably straight forward but any help is appreciated.
Thanks