Rosco22

Got a customer that doesn't want to run a new SWA from the house as I suggested cos its a tricky run and has a 2.5 tne in place already.
I was under the impression i couldnt use this as a distribution circuit for a small DB am i right. Or can i put it on a 20rcbo in the house with a main swich 2 way DB in garage and run a 16a radial and a 6a lighting. He wants 4 double sockets a pond pump an electric door and gate plus 2 outside lights and 2 twin 5fts.
Any ideas appreciated
 
I cant see a problem with you putting a 20A rcbo on the 2.5 tne as long as the cable is mechanicaly protected going from the house to the garage (if the cable is going outside the house) and the load he is intending to use is not over 20A.
How is the 2.5tne routed?
 
Last edited:
also depends on the length of the run. over 25m and there will probably be problems with VD.
 
Electric door, and gate, plus lighting, and sockets, it sounds like its pushing that 2.5mm a bit. Especially when he starts up his compressor, battery chargers etc.
 
Yer that's why I thought I would get some advice as I'm tempted to turn it away unless he upgrades the cable. It's only a 12m run and the gate an door only take an amp each but the pond takes 4amps and he wants to plug in a f/f, battery charger and maybe electric drill now and again. Unless I limit it to 1 double and if he decides to plug an extension in its down to him?
It's in steel tube underground btw.
 
It's in steel tube underground btw.

Is there any room left in the steel tubing for another cable? Could always double up on the 2.5mm & parallel wire....
 
DON'T TURN IT AWAY! If he won't pay to upgrade the cable just fuse it down at the supply, if it trips when he overloads it, he's was warned.
If its in steel conduit can you not yank new cable through using the old?
Like you say 20a RCBO, if you're feeling mean 16a!
 
as above. as long as the PD is 20A, then it's his problem if he has tripping issues. you will have installed to regs.
 
Well that's cleared it up thanks. I haven't looked at weather I can get to the tube think its well buried in the house but will have a closer look when I go to do the job.
 

Reply to garage install in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
199
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
502
Hopefully there's an RCD feeding the garage Cu.
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top