N

ngoodson1969

Hi all,

Could somebody tell me how to supply 2 double sockets and a light to a garage across a garden lawn (approx 5m)? The CU in the house has no RCD protection but has space for more MCBs.
Do you need to use 2 SWA cables (one for light and 1 for power) or use 1 to go to a secondary CU in garage?

Sorry if questions sound dopey!!!!
Cheers
Nick
 
I think the best way to add power would be to take SWA from your existing board off a new MCB, then inside the garage add a RCD 2 way board like this one here: Wylex 2-Way Metal RCD Garage Consumer Unit - Screwfix.com, Where the Trade Buys

Don't forget though you need to bury the cable at least 700mm under grass and add warning tape over the top of the cable before re burying

You also need to take into account the load you expect to be used and also the length of SWA used. A good calculator is here: Cable Size Selector Calculator and online cable selector for electricians keep in mind that 2 double sockets could quite easily use 12KW if you had each at maximum load although for most instances this would be very rare.

I don't mean to sound insulting, but are you a qualified electrician? I believe any work on new circuits need to be notified and also would be subject to inspection by your loocal council unless you are in an approved electrician scheme.

Hope this helps
 
Last edited by a moderator:
Thanks, yes, I know about burying it, I think it's 500mm though.
I am a newly qualified domestic installer but have never actually installed any SWA.
Yes, have seen these garage units, deffo the way to go.

Cheers
Nick
 
Hi

Buried cables shall be at a sufficient depth to avoid being damaged by any reasonably foreseeable disturbance of the ground. About 600mm for the cable or 450mm if you use ducting should do it, depending and use of ground. Eskimo I would be surprised if the regs book gives you a depth if it does please put the reg on here.
Regards
 
Hi

Buried cables shall be at a sufficient depth to avoid being damaged by any reasonably foreseeable disturbance of the ground. About 600mm for the cable or 450mm if you use ducting should do it, depending and use of ground. Eskimo I would be surprised if the regs book gives you a depth if it does please put the reg on here.
Regards

What about:

522.8.10

Appx 4 table 4A2 Item 70 - 73 I think this is were you are seeing the 700mm bit.

and I know its for a caravan site but 708.521.1.1

Carl
 

Reply to Garage Power in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top