Viewed a job today, to reconnect a garage supply and would appreciate your thoughts.
Main board in a shop and garage is for storage ( low use) for a different occupier, so can't
have any faults in garage tripping out shop.
Swa already exists and is 22m in length and 4mm 3 core. It runs half its length along the side of the building and then down through concrete to the garage.
The main board is TT, and the swa will be rcd protected from here on a 32A breaker.
The garage will have a 40 amp rcd protected builders supply unit, an earth rod, bonding to a water supply and two circuits 6amp lights and 16 amp radial.
As the swa is a bit small and bearing in mind voltage drop, I think I'm ok to run the circuits I've specified in the garage?
Or am I forgetting something?