I have been ask to look at supply a shed/summer house with a supply for a s/outlet and a light. Due to the small load I was going to spur from a socket, swa to shed then a little 2 way cu. this is because the run from the d/b is complicated and involves a lot of remedial work that the customer does not want. My query is what about earthing for the shed. The house is on a tt system, do I have to provide a earth spike or can I export from the met. I am a little worried about my ze reading not being low enough. Also I am a little bit concerns about no discrimination between the shed and house d/b

Many thanks
 
if you are going to spur from a socket with a 13A FCU, no protection is needed in the shed ( except to fuse down to 5A fot lighting) assuming the circuit you are coming off id RCD protected. you can add another earth rod at the shed, no problem.
 
Last edited:
Thanks for the reply,

It is RCD protected as it has RCD as main switc. With an fcu to feed the shed then I will do away with the 2 way board and just fuse down the lights. Would you recommend an earth rod? I have heard different theory's and the regs do not clear it up for me
 
i would fit an additional rod. it may even reduce the Ze of the whole installation. can't do any harm anyway. your problem is going to be that a fault in the shed would trip out the whole house. the ideal way would be to replace the CU with a hi-integrity board and feed the shed from a non-RCD circuit, then RCD in shed, but, as you say, it's a problem feeding from CU, so the FCU option is the easiest and cheapest. just make sure you use a double pole FCU so that you can easily isolate both L and N to the shed in case of a FAULT.
 
i would fit an additional rod. it may even reduce the Ze of the whole installation. can't do any harm anyway. your problem is going to be that a fault in the shed would trip out the whole house. the ideal way would be to replace the CU with a hi-integrity board and feed the shed from a non-RCD circuit, then RCD in shed, but, as you say, it's a problem feeding from CU, so the FCU option is the easiest and cheapest. just make sure you use a double pole FCU so that you can easily isolate both L and N to the shed in case of a FAULT.
not RCD the feed to the shed?...on a TT Tel?...high integrity board with an s type in there....then 30mA in the shed.....
 
Thanks for the reply,

It is RCD protected as it has RCD as main switc. With an fcu to feed the shed then I will do away with the 2 way board and just fuse down the lights. Would you recommend an earth rod? I have heard different theory's and the regs do not clear it up for me

On a TT system, it is always better to have more rods!! But if your going to install an earth rod use at least 2 X 1.2m 5/8'' rods coupled together to give you a decent depth and there-by rod stability. Linked together either directly or via EMT or the steel wire armour of your supply cable...
 

Reply to Garage supply and earthing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
658
loz2754
L
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
821

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top