Got a job coming up soon, supply to a garage 35 meters away from exitsing CU. Plan on spliting the tails and taking a SWA via a isolator and 32A MCB unit to the garage. At the garage will be a 16A for socket raidel and 6A for lighting points.

Questions
Am i right in that the SWA does not need RCD protection from the isolator to the gaage cu (protected for OC and SC by 32A MCB)

I have worked VD at around 8.5v does the 6.9 v limit apply to this circuit as the garage will have light points or does 11v max apply as this is a supply cable?

Eathing - Will the 6.0mm earth from the SWA be ok as earth or will i need to spike? (TN-S at house incomer)
 
Hi.

As you have a TN-S supply, no need for a rod, the earthing system of the house is fine to use.

The sub-main itself doesn't need RCD protection.

The VD limit is 3% (6.9V) as you are supplying lighting circuits at the end of it.

:)
 
I thought if the swa is being buried then it should be rcd protected,as its probably running through the garden it will be a special installation.

SWA isnt been burried.

Anywhere outside is a specical location, above or below. But not sure now if RCD is needed? or is it cos of the good protection of the swa no rcd needed. but final circuits will be 30Ma protected.
 
There's no requirement in BS 7671 to RCD protect a buried SWA cable in any location/situation.;)

It must be correctly installed though, there is a reg....522-8-10, also 522-6-2 refers.


Edit.....thought I'd better just add, "unless it's a TT system" to avoid confusion.;):D
 
Last edited by a moderator:

Reply to Garage Supply (SWA feed + 2 Way CU) in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top