timo
Evening all.
Got a job coming up soon, supply to a garage 35 meters away from exitsing CU. Plan on spliting the tails and taking a SWA via a isolator and 32A MCB unit to the garage. At the garage will be a 16A for socket raidel and 6A for lighting points.
Questions
Am i right in that the SWA does not need RCD protection from the isolator to the gaage cu (protected for OC and SC by 32A MCB)
I have worked VD at around 8.5v does the 6.9 v limit apply to this circuit as the garage will have light points or does 11v max apply as this is a supply cable?
Eathing - Will the 6.0mm earth from the SWA be ok as earth or will i need to spike? (TN-S at house incomer)