View the thread, titled "Garage Supply..." which is posted in Australia on Electricians Forums.

The garage I'm about to do is a second garage near an already existing garage. The supply to garage one is in 6mm and 4mm from garage one to garage 2 (only a run about 10m). 4mm surely enough as it's only going to be 10x 58w lights and 6 double sockets (i'll just stick them on a radial). I've always put 6mm to garages but that's because it's only ever been one garage not a second!
 
4mm will be fine, as long as heavy welding equipment is not intended, I would fuse the radial at 20 to be on the safe side, and 5 for the lights coming off a 30amp switch fuse in garage (1)
 

Reply to the thread, titled "Garage Supply..." which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top