L
liam b
Hi,
would it be bad practice to run a supply to a garage through the house loft in 6mm pvc/pvc from main house DB and into an enclosure to run 6mm SWA outside to garage?
just to keep costs down on cable
thanks
Thats fine. Run 6mm from db into an enclosure. And then use proper sw glands to gland swa to enclosure. Id recommend you use 3 core rather than relying on the swa as a cpc. However make sure armourings are properly glanded to garage db and connected to earth. Its only essential to earth armourings at 1 end. Hope this helps.
Robo
i use twin and earth in the house mainly because its easier to install into an insulated CDU , what you could do is gland it into a galve u box and use a 20mm stuffing gland for the 6mm then terminate in a 30 amp chocolate block with a fly lead to earth the box fix to the wall and armour lid on job done
cheers for the replies
my concern was changing from a 2.5mm earth in the pvc to a 6mm earth in the swa.
there will be a metal enclosure in the loft that will be earthed and one above the CU in the garage where i can gland into and run the cores straight through into the garage CU, sounds like its fine
thanks again.
thanks again.
Not all 6mm has a CPC of 2.5mm some 6mm has a CPC of 4 mm ,i insist that the 6m i use has a CPC of 4mm not 2.5
of course the armour is designed for use as cpc. that's why the regs. say we musn't use it as cpc. DOH
Garage SWA
Australia
liam b,
Risteard,