Garage wiring | on ElectriciansForums
Discuss Garage wiring in the Australia area at ElectriciansForums.net
Mark.W
Swindon, Wilts
Guys
I don't have my regs book on me at the moment so looking for some advice please!
I have been asked to install power to a garage, at the moment there is a light which is fed from the d/b to an FCU in the garage (about 5m away), it's on a 16A MCB protected by a 30mA RCD. The cable from the d/b to the FCU is currently 2.5mm. What are the regs about installing a small ring and the lighting from 1 FCU? or would I need to get a 2way d/b in the garage? Would the cable from the house need upgrading?
He only wants 2 double socket outlets in the garage and 2 x lights (1 x fluorescent and 1 x spot light over work bench).
Thanks all:D
Mark
The only reason to upgrade the cable is either due to additional load, distance or route etc.
2.5 is fine on a 20A mcb.
It all depends on what the homeowner is going to be using in the garage.
I did one last week.
I ran 2.5mm from the main CU on a 32A breaker into a garage CU, the garage CU had a 30mA RCD, I then took a 16A for a radial and a 6A for 2 x floris. I also ran it from the RCD side of the main CU to protect the cable run that went through to the garage via wall mounted conduit.
I was going to run 6mm from the CU as the garage CU came with a 32A for a ring, so to save money I popped in a radial on a 16A.
A few weeks back I also did one for a tight sod!!.. To save him money I FCU'd it at both sides of the circuit and then ran a 2 gang socket from the FCU in the garage and then ran a fused spur from that for a light.
Sorry I thought you said you ran a 2-5 on a 32 amp breaker for a second???
getting back to the original question why not run the 2-5 on a 20 amp with the sockets on it then put a switch spur up for the lights
Reply to Garage wiring in the Australia area at ElectriciansForums.net
Received guidance from a logical soul on the Kawie Riders forum: Acc Fuse Block Power to BAT LOAD, install new cable from BAT LINE to AUX + (and)...