Got a customer that is toying with the idea of a garage supply for some welding gear and a plasma cutter. As it stands at the moment he has a TN-C-S arrangement and 100A Bs1361 service fuse and 32A RCBO type B breaker in his consumer unit. It is feeding a 2 way garage board with a 16A and 6A breaker. When using his 2KW transformer it is sometimes tripping and has decided on beefing up the supply.

My question is if I come off a henley block just after an isolator, but before the consumer unit and then feed from a 63A isolator in 16mm SWA would you still recommend TT'ing the garage? The run from the house is approx 20 metres.

Kind regards,

Chris
 
Ok. I'll hazard a guess that the 16a mcb is tripping!

Edit: as it's a type b and should probably be a type c
 
Last edited by a moderator:
Yes the rcbo is tripping via the transformer on the odd occasion and he is wanting to use more gear. As it stands its a small welder and the 2kw transformer, but he wants to put in some more lighting and introduce a larger welder and plasma cutter. He has informed me the welder he wants is on a 16A plug and wants to beef up the supply to his garage.

If he was just keeping what he had then I wouldve just changed it to a type C MCB, but what he has wont stand up to running bigger gear.
The question was more about earthing arrangements if I were to do this.

Kind regards,

Chris
 
I have. Just once back in '67 I think and it was a bad experience which I have no desire to repeat.

I was the Black Sheep of the band because I was the only one who didn't "do drugs".

Good for you mate, I got caught up in Amsterdam with the dodgy cake, never again, seen too much heartache due to drugs.
 
Yes the rcbo is tripping via the transformer on the odd occasion and he is wanting to use more gear. As it stands its a small welder and the 2kw transformer, but he wants to put in some more lighting and introduce a larger welder and plasma cutter. He has informed me the welder he wants is on a 16A plug and wants to beef up the supply to his garage.

If he was just keeping what he had then I wouldve just changed it to a type C MCB, but what he has wont stand up to running bigger gear.
The question was more about earthing arrangements if I were to do this.



Kind regards,

Chris
Refer to the manufacturers guide as to protective device size, they are now required to inform you in the installation guide or user instructions... as we don't know what hes getting then our advice can at best only be speculative and may be wrong and finally why would you want to TT the garage is their a reason why?
 
Personally no reason I would want to TT a garage, but I wasn't really seeing what others felt. In terms of load its speculation as he does not have the gear as yet, hence putting in 16mm swa with a 63A backing that up.
 
If you use a 16mm swa with 3cores then the 3rd core can be earth and used for any bonding requirements in the garage ...the armour will be also earthed for the needs of the circuits, if you have no structural or incoming services in the garage that require equipotential bonding then you could just use a 2core swa and utilise the armour as the earthing for the circuits, but I'd still be inclined to fit 3-core anyway because the welder etc may require type D's large mcb's and this has a tight ELI to meet.

Problem with plasma cutters and welders etc is the inrush and if you get the protection wrong you get nuisance tripping thats why you need to wait to he's decided what hes getting it may alter the set-up of your install.

You could play it safe and use a switchfuse up front with 63amp HRC fuses in and then hope he gets nothing too hefty but with respect your average plasma cutter is not designed for domestic set-ups so Ill play that one by ear.
 
I generally earth the armour at source and use a core as the functional earth. Thanks Darkwood, that was pretty much what I was thinking in terms of design and you've put my mind at ease.

Regards,

Chris
 

Reply to Garage wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
868

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top