I have a set of double insulated LED garden brick lights that I installed about 5 years ago, Recently they tripped the RCBO and would not reset. The fault is L&N to earth, about 0.2 mega ohms. The install is SWA terminated into galvanized conduit boxes filled with magic jell.Thinking the jell may have become absorbent after time I split the circuit and opened some of the boxes removing the jell as I went. the test result was the same. I then started cutting out the push fit connectors and testing each leg, these were all clear. When I tested a line conductor of one of the disconnected fittings to the metal of the conduit box it was down to earth, I removed the flex from ythe light for closer inspection and it looked fine. I had the same issue a couple of years ago with another set of garden lights which I just changed and they worked fine afterwards but now I want to know how this is possible or what I am over looking, any sensible suggestions?
 
Did you remove the lamps when you tested IR L to N? daft question but sometimes even the simplest things are overlooked
 
It's a Line-Earth fault Pete.

If I'm reading this right, all your cables are fine, the fault's in the luminaires?
Sounds like the usual moisture ingress, get better quality lights.
 
I had a garden light insulation fault last month, the large base of one of the lanterns on a wall was filled with an ants nest!
Damp seems to get in and can cause tracking in all sorts of places. What was the lights cable type?
 
On the basis that Ive never been able to find brick lights with a 'better' rating than IP65, I'm going to assume you couldn't either. I don't fit any brick lights anymore because of this reason.

IP67 or preferably IP68 for me if its going to be 'buried' in a wall/the ground - had enough of going back for the same reasons you have.
 
The lights Are IP67 Aurora sealed fittings with two core rubber flex that went through a stuffing gland into a box filled with jell. In rights there should be no way moisture can get in however it sounds like the only logical explanation
 

Reply to Garden light fault in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
896
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top