Hi guys . Doing a garden lighting project for a friend . The house supply is tn-s the lighting circuit is on its own 6amp type A rcbo. Armoured cable feeding 8 type 1 led spike lights via ip rated junction boxes via photocell. My question is. As it’s a tn-s system would it be best practice to use the earth from main cu. Or TT it. My only worry was if the grass was soaking wet and someone touched the metal light fitting bare footed . Would this cause a problem as there would be two different earth paths . Does that make sense or have I got that one wrong . I am a qualified electrician but don’t really do much domestic work so don’t really have to think about this sort of thing often.