Garden lights | on ElectriciansForums
Discuss Garden lights in the Australia area at ElectriciansForums.net
M
mickys86
Got called out today to look at some garden lights which are only 12-18 months old because they keep tripping the rcd. When I get there I have a look and I find armoured coming out of the house and going into a ip rated jb which is buried underground. What then happens is non armoured flex joins to another jb and 6 garden lights are then all connected via non armoured flex which is buried underground and running for several metres. Four of the cables have breakdown in the insulation and the solution I had after playing about with two of the lights is to reinstall the lights using SWA etc.
My question is....
Is burying non armoured flex against regulations or just bad practice (because it's on an rcd) because personally I wouldn't do it, rcd or not
Cheers,
Michael
Well i havent a regs book to hand but im sure theres something along the lines of providing adequate mechanical protection and also protection against external influences which would come to mind.
not sure if this is the right answer to you but
reg 512.2 external influences
512.2.1-equipment shall be designed appropriate to the situation in which it is to be used or its mode of installation shall take account of the conditions to encountered
512.2.1-if equipment by its construction, have the characteristics relevant to the external influences of its location, it may be used nevertheless be used on condition that it is provided with appropriate additional protection
So I guess it should've been done in SWA but it's all fine to bury flex if on an rcd?. It's all quite contradictory haha. Cheers for finding it, I'm still not home and the book is gonna be opened when I get in :)
The guy that did this was a fully qualified sparks coming
Out of a big company to go out on his own, and yet I'm new to the trade and though I don't know everything (I'm not naive to think that I could know everything) I know that a cable has to be mechanically protected. To think that people do this is really frustrating!!
Reply to Garden lights in the Australia area at ElectriciansForums.net
As littlespark says there's no ways you're going to find spike lights that can accomodate SWA cables directly into them.
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...