Hi all,
Upgrading a consumer unit and bonding for a customer and would welcome any ideas.
Domestic property TN-S 100A incomer, run in a new 10mm bond to water and there is already a 10mm in the MET which I assumed to be bonding for the gas.
Gas meter is out the front of the house in a cupboard, no clamp there, no probs I'll find it where the pipework enters the house. Wrong!
I have taken down lots of boxwork, coving etc around boiler and gas fire and can
I used a wander lead to test continuity from the 10mm earth cable, removed from the MET, to gas pipework at the meter and before the regulator in the boiler and got low resistance continuity 0.09 ohms.
How would it be best to record this on EIC?
Any advice appreciated
Shane.