Hi all,
Upgrading a consumer unit and bonding for a customer and would welcome any ideas.

Domestic property TN-S 100A incomer, run in a new 10mm bond to water and there is already a 10mm in the MET which I assumed to be bonding for the gas.

Gas meter is out the front of the house in a cupboard, no clamp there, no probs I'll find it where the pipework enters the house. Wrong!

I have taken down lots of boxwork, coving etc around boiler and gas fire and can
I used a wander lead to test continuity from the 10mm earth cable, removed from the MET, to gas pipework at the meter and before the regulator in the boiler and got low resistance continuity 0.09 ohms.

How would it be best to record this on EIC?

Any advice appreciated

Shane.
 
Acceptable result. It is effectively bonded.

Record it as so and state 'not inspected' and 'cannot be inspected' blah blah and sleep happy in the knowledge that you have done your utmost.

:)
 
Thanks for replies,
I just realised 0.09 ohms reading was beofre nulling the wanderlead, doh! actual reading is 0.02 ohms. I guess this is better.

Cheers
Shane
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Gas Bonding??
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
ShaneD,
Last reply from
electricAl,
Replies
6
Views
2,584

Advert

Back
Top