Gas meter 'vs' SWA cable proximity | on ElectriciansForums
Discuss Gas meter 'vs' SWA cable proximity in the UK Electrical Forum area at ElectriciansForums.net
sythai
Devon, United Kingdom
Hi Guys
Would I be correct in thinking an electric cable can be as close as 25mm to a gas meter ?
(not that I'd ever be that close out of choice)
Or is it the 150mm reg as with proximity to consumer units, sockets, accessories...
Had a quick scan in my on-site guide but not so clear - been a long day !
Thanks Sy
Pretty sure there is a gas reg that states the gas shouldn't be within 150mm of the electric incomer, other than this instance I think the 25mm guidance applies. I was told that these rules are to do with arcing which is unlikely to be an issue with swa
This is the gas regulation:
BS6891-2005
8.16.2 Separation of installation pipework from other services
Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows:
a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
Reply to Gas meter 'vs' SWA cable proximity in the UK Electrical Forum area at ElectriciansForums.net
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...