Gas Pipe Bonding Question | on ElectriciansForums

Discuss Gas Pipe Bonding Question in the Australia area at ElectriciansForums.net

H

horsleya

I have a question regarding my own property which does not appear to have any main bonding on the Gas Pipe. The Gas meter is in a box on the outside of the house. the feed comes into the house at Three seperate points. One at the front for the gas fire, once along the side wall for the Gas Boiler and once at the back for the Kitchen Cooker.

The question is where do you connect the bonding? The CU is nearest to the Boiler.
I understand that the connection should be close to the Gas Meeter but as this is outside should it be connected outside or at one (or all) of the points of entry into the building?

Hope that is clear!
Thanks
 
For a service pipe, the main bonding conductor should be connected as near as possible to the point where the service enters the building.
The connection must be before any branched pipework and on the consumers side of any meter.
If possible the connection should be made within 600mm of the meter outlet.
Where the meter is outside, the bonding connection should be made at the point of entry of the service into the building. 544.1.2
 
That is where my issue arises.
The pipe enters the house at three seperate places all of which are greater then 600mm from the Meter.
The Meter is in a box on the side of the house.

So connecting within the Meter Box (albiet outside of the house) sounds sensible to me as the alternative would be at three seperate entry points to the building all of which are greater then 600mm from the Meter and all would be after a Junction as the T's are outside.
 
Last edited by a moderator:

Reply to Gas Pipe Bonding Question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
611

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top