Hi finchy,
We generated 1290 kWh in the three month period from 1st March to 1st June 2012. May was an exceptionally sunny month.
The system comprises 15 REW Premium 240W panels (Nominal 3.6 kWp but claimed to have positive tolerance of +7% to +12% giving expected 3.92kWp from the system) set on a 22.5 degrees roof pitch, angled at 10 degrees East of South and feeding a Sunny Boy 4000TL-20 inverter.
I have calculated the equivalent output for our system for the three months including May based on the ratio of the two system kWp figures and got 575 kWh. This is about 8% below the 620kWh that EON disputed but above their calculated figure of 547kWh. Our roof angle is very shallow and below the optimum, so could easily account for the difference in output between our systems.
I had a look at Ofgem's document on their website:- "Feed in Tariff Scheme: Guidance for Licensed Electricity Suppliers" and found the paragraph 2.13.iv) in the section "Responsibility on all FIT Licensees" which states:-
2.13.iv) taking all reasonable steps to acquire Generation Meter Readings and satisfy themselves that these Generation Meter Readings are reasonable and within Expected Tolerances for that particular Installation (see Chapter 7); and if applicable, Export Meter Readings at least once every two years (see Chapter 7);
So, I understand where EON are coming from. However, they are clearly being unreasonable and may need help to understand this. The Ofgem website offers an email address:
[email protected] and a telephone number 020 7901 7290, so they may be able to provide guidance with dispute resolution.
Good luck.